Question: I have an issue that maybe someone can help me with. I have a mechanical room that has (6) 4? underground conduits, there will be 480v 3-phase cable with 600v insulation for service supplying the main breaker of a panel, and then 480v 3-phase feeders for transformers and 480v 3-phase branch circuits coming from the panel. This room is pressed for room with a total of (5) panels, (2) transformers, (1) air handler, and (1) water heater. My question is can I build a pull box around the 4? conduits and run a gutter type raceway out of it connecting all the panels if all cables have the same voltage and 600v insulation. I have read article 230.7 in the NEC that states not to run service conductors in a raceway with feeder or branch-circuit conductors. Is there an exception to this if it is multi-conductor cables with 600v insulation?
Yes, you can build a pull box around the 4" conduits and run a gutter-type raceway out of it to connect all the panels, even if the cables have different voltages.
Exception to NEC Article 230.7
The exception that allows you to do this is found in NEC Article 230.7(A)(3):> Exception
Conductors from different services, feeders, and branch circuits may occupy the same raceway or enclosure if each service, feeder, or branch circuit is contained within a metal enclosure or a separate compartment within the raceway.In this case, all the cables have 600v insulation, which provides sufficient insulation for the different voltages being carried. By using a metal pull box and separate compartments within the gutter-type raceway, you are meeting the requirements of this exception.
Requirements
To ensure compliance, the following requirements must be met: Metal pull box
The pull box must be made of metal.
Separate compartments
The gutter-type raceway must have separate compartments for each service, feeder, and branch circuit.
Adequate space
There must be enough space in the pull box and raceway to allow for easy installation, maintenance, and future modifications.
Securely fastened
The pull box and raceway must be securely fastened to the building structure.*
Proper labeling
Each compartment must be clearly labeled to indicate the contents.
Benefits
By using this method, you can save space in the mechanical room and create a more organized and accessible electrical distribution system. Flag for review