Topic: Art 517 Isolated Power

User: augie47, Location: Tennessee

Asked on: Friday, March 4, 2011 at 7:28 pm EST
Answered on: Tuesday, May 14, 2024 at 2:22 am EDT

Question: An E/C working in a jurisdiction adjacent to mine is wiring a hospital operating room with isolated power supplies. He was asked by an inspector about a bond wire installed in the wall interconnecting the metal studs to the isolated power supply.I knew of no such requirement. Have I overlooked something ?

Yes, you have overlooked something. The 2017 NEC requires that metal studs be bonded to the isolated power system in patient care areas. (NEC 517.13) Flag for review