User: jtester, Location: Las Cruces N.M.
Asked on: Saturday, March 5, 2011 at 7:49 am EST
Answered on: Tuesday, May 14, 2024 at 2:22 am EDT
Question: I am stumped by this problem. I have a 277/480 volt service with a 1200 amp GFI protected main breaker feeding a medium sized medical office building. The 8 tenant meters and disconnects are downstream of the main disconnect. Our utility insists on a meter socket with a neutral bonded to the can. Our inspector has identified it as a problem, a violation of 250.142 Ex2 because of the GFI protection on the main. I?ve been looking for 277/480 volt meter sockets rated at 200 and 320 amps with isolated neutrals, with no luck. I am not even sure our utility will allow it, but if they are unavailable, it won?t matter.Has anyone run into this, or have an idea of a solution?
Issue
The utility requires a meter socket with a neutral bonded to the can, but this violates NEC 250.142 Ex2 due to the GFCI protection on the main breaker.
Possible Solutions
Negotiate with the Utility
Try to convince the utility to allow isolated neutral meter sockets. Explain the safety concerns and code compliance issues.
Consult with the Authority Having Jurisdiction (AHJ)
Discuss the situation with the electrical inspector to see if an alternative solution can be approved.
Use a Non-GFCI Main Breaker
Replace the GFCI main breaker with a standard main breaker. This would eliminate the code violation, but would also forfeit the GFCI protection.
Install Separate Metering Equipment
Install separate metering equipment for each tenant downstream of the GFCI main breaker. This would isolate the neutral and comply with the code.
Use a Meter Socket with a Neutral Grounding Resistor
Locate a meter socket with a built-in neutral grounding resistor (NGR). The NGR would limit fault currents and potentially allow the use of an isolated neutral socket.
Contact a Specialty Manufacturer
Reach out to electrical equipment manufacturers who specialize in custom or unique solutions. They may be able to provide a custom-made meter socket that meets the requirements.
Additional Considerations: Ensure that all other applicable codes and standards are met, such as NEC 250.24(B)(2). Document all communications and approvals with the utility and AHJ.* Consider the cost and feasibility of each solution before making a decision. Flag for review