Topic: Number of UL listed devices in an assembly

User: xoxota, Location: Tennessee

Asked on: Saturday, March 5, 2011 at 11:49 am EST
Answered on: Tuesday, May 14, 2024 at 2:22 am EDT

Question: I have an control panel composed of 7 UL listed devices. Where does it say that this control panel has to be fabricated at a shop and have the UL bug on it? I seem to remember someone saying that if the assemble is composed of 7 or less UL listed devices, it would need to be assembled at a shop. Can anyone attest to that?Thank you!

The UL Listing of the control panel is not dependent on how many UL listed components are within it or where it is manufactured. A device can be UL Listed whether it is assembled at a shop or in the field. Additionally, a device can contain UL Listed components from different manufacturers and still be UL Listed itself. As long as the complete control panel meets the requirements of the UL standard that it is being Listed under, the UL Listing of the control panel is not affected by the number of components within it or its location of assembly. Flag for review