Topic: Help with 400 amp resi pedestal install

User: jjhoward, Location: Northern NJ

Asked on: Saturday, March 5, 2011 at 8:16 pm EST
Answered on: Tuesday, May 14, 2024 at 2:23 am EDT

Question: Cust has existing underground 200 amp service. He is looking to add about 100 amps of load in a shop by his attached garage. Load analysis for his existing home is 190 amps. (2 large A/C units, elect dryer, elect range, pool)Presently the underground feed comes off a utility pole on his property about 110' from his house.Was considering installing a 400 amp pedestal at the pole and bringing a second set of 200 amp conductors to the house. Install a second 200 amp panel and use this 2nd panel to feed his shop.Is it code complaint (2008) to only have the 2 200amp disconnects at the main breaker panels? These panels will be placed next to each other. No disconnect at the pedestal.Thank you.

Yes, it is code compliant under the 2008 NEC to only have the two 200-amp disconnects at the main breaker panels, without a disconnect at the pedestal.

Section 230.70(A)(1) of the 2008 NEC states

> "General. Each service disconnecting means shall disconnect all ungrounded conductors that supply or pass through the overcurrent device."Since the two 200-amp disconnects at the main breaker panels disconnect all ungrounded conductors that supply the house and the shop, they meet the requirements of Section 230.70(A)(1).

Section 230.70(C) of the 2008 NEC states:
> "Combined Disconnection. Where the disconnecting means for feeders or branch circuits is grouped at a common location, there shall be a main disconnecting means that will simultaneously disconnect all feeders or branch circuits at the building or structure."Since the two 200-amp disconnects at the main breaker panels are grouped at a common location and will simultaneously disconnect all feeders that supply the house and the shop, they also meet the requirements of Section 230.70(C).Therefore, it is code compliant under the 2008 NEC to install a 400-amp pedestal without a disconnect and connect it to two 200-amp panels in the house, one for the house and one for the shop. Flag for review