User: wmeek, Location: Texas
Asked on: Monday, March 7, 2011 at 9:21 am EST
Answered on: Tuesday, May 14, 2024 at 2:25 am EDT
Question: I have a 20HP 230v 3phase motor on a Portable Chop Saw. Table 430.250 says to use 54A.Using table 400.5 Column A would a #4 be correct for wiring a 20hp chop saw. This saw is on a rolling platform to be able to move around to keep from having to lift these wire ropes very high off the floor to be able to cut them. Was going to run this SO cord from a 100A Non fused disconnect. Ckt is being fed from a breaker in a panel sized per 430-52. Is this a installation code compliant.thanksI have a 230v - 3phase - 20HP Wire rope Saw, that is mounted on its own platform with wheels to be able to roll around close to floor to have from having to lift the cable up very high to cut it off. I am looking for some help in wiring this equipment. If you use table 430-250 for a 20hp = 54A.54A x 125% = 67.5A I will have to use a #4 thhn Branch circuit conductor per 430-250 and54A x 250% = 135A I will have to use a 150A Breaker per 430-6 & 430-52Customer wants this wired with a receptacle a SO type installation so to have a little portablitiy.54A x 125% = 67.5A Need a #2 Type SO per 400-5The total distance from Panel to receptacle is 115'Distance from receptacle to saw (30' of SO cord)If this is correct sizes of conductors and breakers, What type and size of receptacle could be used . Also the problem I have had in the past is the conductors are usually to big to land in the controller of the equipment.Thanks
Conductors and Breaker Sizes
Branch Circuit Conductors
#4 THHN (Table 430.250)
Breaker
150A (Table 430.6 and 430.52)
Receptacle and Plug Caps
Receptacle
50A, 3-pole, NEMA L6-30P (Table 400.5)
Plug Cap
50A, 3-pole, NEMA L6-30R (Table 400.5)
SO Cord
Conductor Size
#2 THHN (Table 400.5)
Length
30'
Installation
The installation should be in accordance with the requirements of Article 430, Part III of the NEC. The following is a summary of key requirements: Use a separate circuit for the chop saw. Install a lockable disconnect within sight of the controller of the chop saw. Protect the circuit with a circuit breaker or fuse in accordance with Table 430.52. Ensure that the disconnect and electrical components are suitable for outdoor use if necessary. Provide adequate slack in the SO cord to allow for movement of the chop saw.
Controller Wiring
The #4 THHN branch circuit conductors should be terminated in an approved junction box at the controller of the chop saw. Use appropriate wire connectors or terminal blocks to connect the conductors to the controller terminals. Use a strain relief to secure the conductors within the junction box.
Compliance with NEC:
The proposed installation appears to be compliant with the requirements of the NEC. However, it is important to verify all aspects of the installation with your local Electrical Inspector to ensure compliance with local codes and regulations. Flag for review