Question: I do not have my code book here at the facility right now, any help is appreciated. On a 3-wire circuit (12-3 cable) run to a double duplex receptacle, with each single being a seperate circuit, is a two pole breaker required? If so, what is code reference? Thanks.
Yes, a two-pole breaker is required.Code Reference
*
National Electrical Code (NEC) 210.4(E)(4): "Where a 3-wire circuit is used to supply two or more 120-volt branch circuits, a two-pole circuit breaker or two single-pole circuit breakers shall be employed."Reason:
Using a two-pole breaker ensures that both single circuits are disconnected simultaneously when there is a fault, providing enhanced safety. This prevents the possibility of one of the circuits being energized while the other is de-energized, which could create a hazardous situation. Flag for review