Question: Two machines and a lighting load are connected in parallel to a 220 V, 60 Hz line. The first machine uses 40 kW of power at 0.81 power factor lagging. The second machine uses 27 kVA at 0.93 power factor leading. The lighting load consumes 13 kW. What is the current in the line feeding the three loads? What kVAR value of capacitance connected across the line is necessary to obtain a power factor of 0.98 lagging? With this capacitor installed, what will be the current flowing in the line feeding the four loads?Could any one help me with this one?Thanks!!
Step 1: Calculate the current and power factor for each loadMachine 1
Apparent power (S1) = 40 kW / 0.81 = 49.4 kVA Current (I1) = S1 / V = 49.4 kVA / 220 V = 224.5 A Power factor angle (θ1) = arccos(0.81) = 36.9° lagging
Machine 2
Apparent power (S2) = 27 kVA Current (I2) = S2 / V = 27 kVA / 220 V = 122.7 A Power factor angle (θ2) = arccos(0.93) = 21.8° leading
Lighting load
Current (I3) = 13 kW / 220 V = 59.1 A Power factor angle (θ3) = 0°
Step 2: Calculate the total current and power factor Total apparent power (ST) = S1 + S2 Total current (IT) = √(I1^2 + I2^2 + I3^2) Total power factor (PF) = (ST) / (IT V)Plugging in the values: ST = 49.4 kVA + 27 kVA = 76.4 kVA IT = √(224.5^2 + 122.7^2 + 59.1^2) = 274.6 A PF = 76.4 kVA / (274.6 A 220 V) = 0.95 laggingStep 3: Determine the kVAR value of capacitance needed
To achieve a power factor of 0.98 lagging, the total reactive power (Q) should be: Q = ST (1 - PF) = 76.4 kVA (1 - 0.98) = 1.53 kVARThe capacitor should provide this reactive power: Qc = 1.53 kVARStep 4: Calculate the current with the capacitor installed
With the capacitor installed, the total current (IT') becomes: IT' = IT PF / PF' IT' = 274.6 A * 0.95 / 0.98 = 268 ATherefore, the current in the line feeding the three loads is 274.6 A, and the kVAR value of capacitance needed to obtain a power factor of 0.98 lagging is 1.53 kVAR. With the capacitor installed, the current flowing in the line feeding the four loads is 268 A. Flag for review