Topic: Supporting a light fixture using pvc coduit

User: whatrymes, Location: Massachusetts

Asked on: Monday, March 7, 2011 at 5:50 pm EST
Answered on: Tuesday, May 14, 2024 at 2:26 am EDT

Question: Section 347-3(b) in the NEC says that a lighting fixture may not be supported by nonmetallic conduit (pvc.) Is this the same as strapping a box to an outside wall, running pvc (properly bracketed) to the box from a jb at the sill and attaching the light fixture to the box?Thank you,Ed

No, Section 347-3(b) of the NEC is not the same as strapping a box to an outside wall, running PVC (properly bracketed) to the box from a junction box at the sill, and attaching the light fixture to the box.Section 347-3(b) of the NEC prohibits the use of nonmetallic conduit (such as PVC) to support a lighting fixture. This is because nonmetallic conduit is not as strong as metal conduit and may not be able to adequately support the weight of the fixture.However, the scenario you described is not a violation of Section 347-3(b) of the NEC. In this scenario, the light fixture is supported by the box, which is in turn supported by the wall. The PVC conduit is only used to run the wires to the box.Therefore, it is acceptable to strap a box to an outside wall, run PVC (properly bracketed) to the box from a junction box at the sill, and attach the light fixture to the box. Flag for review