User: ohms277, Location: Chapel Hill, NC
Asked on: Monday, March 7, 2011 at 8:56 pm EST
Answered on: Tuesday, May 14, 2024 at 2:26 am EDT
Question: I am replacing main disconnects on each building of an apartment project. There are meters after the disconnect. The POCO requires a #6 ground to the meters socket's neutral connection point. This neutral bar is bolted straight into the meter socket case, and is not isolated in any way. If I bond the grounding electode conductor to the neutral with the green screw in the main disconnect, do I now have a paralel path? Is not the POCO's requirement against the NEC? The AHJ says the POCO is not in compliance with the NEC. The POCO will not energize the service without the above. I reach out to your collective wisdom, to gather ammuntion.
Parallel Path Issue
Yes, bonding the grounding electrode conductor (GEC) to the neutral within the main disconnect may create a parallel path for ground fault currents. This defeats the purpose of the GEC, which is to provide a dedicated path for ground faults to return safely to the earth.
NEC Requirements
NEC requires that the GEC be connected to the equipment grounding conductor (EGC) only at the service entrance or at the first point of service disconnect. This means that the GEC should not be connected to the neutral conductor anywhere else in the system.
POCO's Requirement and NEC Compliance
The POCO's requirement to ground the meter socket's neutral connection point with a #6 ground is not in compliance with the NEC. The NEC prohibits bonding the GEC to the neutral conductor within the service equipment enclosure.
AHJ's Position
The AHJ is correct in stating that the POCO's requirement violates the NEC. The AHJ has the authority to enforce the NEC and may prevent the POCO from energizing the service until the violation is corrected.
Ammunition for Negotiation NEC Article 250.24(A)(5): Prohibits bonding the GEC to the neutral conductor within the service equipment enclosure. NEC Article 250.32(B)(1): Requires the GEC to be connected to the EGC at the service entrance or the first point of service disconnect. Letter from the National Electrical Manufacturers Association (NEMA): https://www.nema.org/Standards/Published-Standards/Pages/Grounding-of-Meter-Sockets-and-Neutral-Busses-of-Multiple-Metering-Enclosures.aspx Technical Bulletins from Electrical Inspection Authorities: Many AHJs have issued bulletins on this issue, supporting the NEC's requirements.
Possible Solutions Isolate the Neutral Bar in the Meter Socket
Install a non-conductive barrier between the neutral bar and the meter socket case.
Use a Grounding Plate
Install a grounding plate that is isolated from the neutral conductor and connect the GEC to the plate.*
Negotiate with the POCO: Explain the NEC requirements and the potential safety hazards of bonding the GEC to the neutral. Explore alternative grounding methods that comply with the NEC. Flag for review