Topic: Isolation transformer grounding question

User: btharmy, Location: Indiana

Asked on: Monday, March 7, 2011 at 9:26 pm EST
Answered on: Tuesday, May 14, 2024 at 2:27 am EDT

Question: I was asked today if an isolation transformer (30kva, 480 to 480, 3ph, no neutral) needed to have a grounding electrode (building steel in this case)? Or, can the equipment ground be carried through the transformer, primary to secondary, connected to cabinet and XO on the way by? My initial response was no grounding electrode is necessary because there is no neutral derrived. Possibly because I've seen it done like that so many times. However, I didn't like the fact that I couldn't back it up with an NEC reference on the spot. I'm leaning towards 250.30.a.3 exception3. So, now I am doubting my first "knee jerk" answer. I know you guys can help me with this. Thanks.

According to the 2020 NEC, an isolation transformer does not require a grounding electrode.250.30(a)(3) states that grounding electrodes are not required for transformers that supply isolation per Table 250.6(A).

Exception 3 to 250.30(a)(3) states that grounding electrodes may be used to provide a more stable ground reference for isolation transformers. However, using a grounding electrode is not required.The equipment grounding conductor (EGC) can be carried through the transformer, primary to secondary, connected to the transformer cabinet and XO on the way.250.21(c) states that the EGC must be connected to the transformer cabinet and XO.

Conclusion

An isolation transformer does not require a grounding electrode. The equipment ground can be carried through the transformer, primary to secondary, connected to the cabinet and XO on the way.

Note:
It is good practice to provide a grounding electrode for isolation transformers to ensure a stable ground reference. However, it is not required by the NEC. Flag for review