Question: A customer called today for an estimate to upgade his service from 200 amps to 400 amps. He is replacing his 5 ton a.c. system with a 3 ton and a 2 ton system and has no more room in his panel. when I told him he probably didn't need to upgrade his service he said he was going to be getting 2 electric cars and they each had a peak recharging load of 80 amps @ 240 volts - a total of 160 amps peak load.I have a hard time believing that, but don't know where to look to verify it.If he is right, where would you find a cord or receptacle rated for 80 amps?
Recharging Load of Electric Cars
It is uncommon for electric cars to have a peak recharging load of 80 amps @ 240 volts. Most residential electric car chargers are rated for 32-50 amps @ 240 volts, resulting in a peak load of 6.4-10 kW.
Service Upgrade Calculations
To calculate the service upgrade requirement, consider the following:
Existing Load
200 amps x 120 volts = 24,000 watts
New AC Systems
Assuming 3 tons at 4,500 watts and 2 tons at 3,000 watts, the new AC load is 7,500 watts.*
EV Charging
If the EV charging load is 160 amps peak, it is equivalent to 38.4 kW (160 amps x 240 volts).
Total Estimated Load
24,000 watts + 7,500 watts + 38,400 watts = 69,900 watts
Required Service
69,900 watts / 240 volts = 291 amps
Cords and Receptacles for 80 Amps
If the EV charging load is 80 amps @ 240 volts, it is unlikely that the customer would need to upgrade his service. However, if he requires a receptacle rated for 80 amps @ 240 volts, it is available from electrical supply houses and can be plugged into a 40-amp circuit.
Recommendation:
Based on the calculations above, the customer may not need a service upgrade to 400 amps. However, if he intends to purchase electric cars with a charging load significantly higher than 50 amps @ 240 volts, he may need to consider a larger service upgrade. Flag for review