Question: i am allowed one dumb question per day.this is it:can you refit t8 strip fixtures to use t5 lamps without changing ballastsand tombstones? someone is telling one of my clients that you can uset5 "adapters" to use t5 lamps in a t8 fixture.i'm googling it, and my b.s. filter is starting to clog up....has anyone done this?and if it is doable, is it worth doing, given the small advantage betweent5 and t8, which seems to be about 10% depending on who you talk to.thanks, guys.... the company who is advocating doing this, is inflorida, and i'm wondering if it's a "other side of the country" thingthat i've not seen on the left coast....randy
Randy,The short answers are no, and it's not worth it to do this.The reason that the "adapters" are being used is to fit the smaller bi-pins for the T5 lamps into the larger tombstones for the T8 lamps. The adapters only allow for the physical fit. The T5 lamps require a higher current than T8 lamps, and they have different needs for starting and running. The ballasts for T8 lamps can't provide these needs, so the T5 lamps won't work properly. Even if they could be made to work, it's not worth the effort for such a small gain.There are new T8 lamps that are just as efficient as T5 lamps, and they can be used without changing the ballasts or tombstones. These lamps are a better choice than T5 lamps, because they are less expensive and they don't require any special adapters.So, if you're looking for the most efficient way to light your space, I recommend using T8 lamps. They're less expensive and they work better than T5 lamps.Hope this helps! Flag for review