Question: Hi, It's been a while since I have been here.A client bought a used wire drawing machine. It consists of 4 125HP DC motors among other loads. Each motor has its own DC drive with its own AC feed. There are molded case circuit breakers inside the drives cabinet doors that disconnect the AC feed. You have to open the doors to get to it. My feeling is this does not meet the controller disconnecting requirements but I need back up. The difference is we will have to set a distribution board ahead of the DC drives with lockable breakers rather that feed directly from a remote board. I am just looking for opinions.Thanks,
NEC Requirement
NEC 430.110 requires that controllers for motors over 100 horsepower (hp) shall be capable of being manually locked in the open position.
Interpretation
The molded case circuit breakers inside the drives cabinet doors do not meet the requirement of being "manually locked in the open position." This is because: The circuit breakers are not readily accessible without opening the doors. The doors may not be lockable.
Proposed Solution
To comply with the NEC, a distribution board should be installed ahead of the DC drives with
lockable circuit breakers. This will allow for manual locking and disconnection of the AC feed to the drives.
Benefits of the Proposed Solution
Improved safety: Lockable circuit breakers provide a more reliable and consistent method of disconnecting the AC feed for maintenance or emergencies. Compliance with NEC: The proposed solution meets the requirements of NEC 430.110.* Convenience: Lockable circuit breakers are more easily accessible than the molded case circuit breakers inside the drive cabinets.
Conclusion:
The molded case circuit breakers inside the drives cabinet doors do not meet the requirement of NEC 430.110 for manually locking the controller in the open position. A distribution board with lockable circuit breakers is required to ensure compliance and improve safety. Flag for review