Asked on: Tuesday, March 8, 2011 at 2:37 am EST
Answered on: Tuesday, May 14, 2024 at 2:28 am EDT

Question: As per NFPA780, Article 3-12.13, Down Conductors (Bare Copper Wire, 50 mm sq) coursed in Reinforcement Concrete Columns shall be connected with the reinforcing steel re-bars at its upper and lower extremities. This down conductor is further coursed to the grounding ring (having several grounding rods) outside the building in order to effectively ground the concrete structure of the building. This process is done in concrete structure buildings having steel re-bars.We have a project in which concrete structure building have epoxy coated steel re-bars and if we chip the epoxy coating of these steel re-bars at upper and lower level of structural columns to connect down conductor within the columns, it will not have a continuous grounding system as compared to the steel re-bars without epoxy coating. Therefore, it will defeat the purpose of structural grounding in the case of Lightning Strike or otherwise. Kindly inform me with some code reference that how can we effectively do the structural grounding for the concrete building having epoxy coated Re-inforcement bars.Thanking you all....

NFPA 780 Article 3-12.13 Structural Grounding(A) Down Conductors(3) Where exposed reinforcement is used as a down conductor, the reinforcement shall be connected to the main grounding electrode system by one of the following methods

(a)

The reinforcement shall be connected directly to the main grounding electrode system with grounding electrode conductors in accordance with 250.110(A)(4).(b) The reinforcement shall be connected to a grounding electrode conductor that is routed uninterrupted to the main grounding electrode system.(c) A grounding conductor not smaller than 8 AWG copper shall be exothermically welded to the reinforcement at the point of connection to the main grounding electrode system.

For Buildings with Epoxy-Coated Rebar

The code does not explicitly address the use of epoxy-coated rebar in structural grounding systems. However, there are several industry-accepted methods for grounding structures with epoxy-coated rebar

1. Use Mechanical Connectors:

Use mechanical connectors, such as grounding clamps or plates, to connect the down conductor to the rebar. These connectors pierce or clamp onto the epoxy coating, allowing for a secure electrical connection without damaging the coating.2. Chip the Coating

Chip the epoxy coating from the rebar at the point of connection. The bare rebar can then be connected to the down conductor using the methods outlined in NFPA 780 3-12.13(A)(3). It is important to carefully chip the coating and avoid damaging the underlying rebar.

3. Use Conductive Paint or Primer

Apply a conductive paint or primer to the epoxy-coated rebar at the point of connection. This conductive coating will allow for a reliable electrical path between the down conductor and the rebar.

4. Use Supplemental Ground Rods

Install supplemental ground rods near the foundation of the building. Connect the down conductor to the ground rods using a grounding electrode conductor. This method provides an alternative grounding path in addition to the rebar.

Note:
It is important to consult with a qualified electrician or lightning protection expert to determine the most appropriate method for grounding a specific structure with epoxy-coated rebar. Flag for review