Topic: How to do insulation test and continuity test on ac lift motor.

User: rajpaul, Location: Macau, China

Asked on: Tuesday, March 8, 2011 at 3:12 am EST
Answered on: Tuesday, May 14, 2024 at 2:28 am EDT

Question: How to do insulation test and continuity test on ac lift motor. Please give me example rating details ,starts/hour and enclosure.

## Insulation TestRating Details

Voltage rating: 460V Power rating: 10hp Current rating: 17.5A

Starts/Hour

12

Enclosure

* Totally Enclosed Fan Cooled (TEFC)

Procedure

1. Disconnect the motor from the power supply.
2. Discharge any stored energy by connecting the motor leads together for 10 minutes.3. Use an insulation tester rated for at least 1000V. Set the tester to 500V or as per manufacturer's recommendations.
4. Connect the positive terminal of the tester to one of the motor leads.5. Connect the negative terminal of the tester to the motor frame or ground.
6. Gradually increase the test voltage until it reaches 500V or the specified test voltage.7. Hold the voltage at the test voltage for 60 seconds.
8. Observe the insulation resistance reading on the tester.9. Record the insulation resistance value.


Acceptance Criteria

The insulation resistance should be greater than 1 megohm. If the insulation resistance is below this value, the motor may need to be repaired or replaced.## Continuity Test

Procedure

1. Disconnect the motor from the power supply.
2. Discharge any stored energy by connecting the motor leads together for 10 minutes.3. Use a low-resistance ohmmeter.
4. Connect the ohmmeter leads to the motor leads.5. The ohmmeter should read a low resistance (less than 1 ohm).
6. Reverse the ohmmeter leads and repeat the test.


Acceptance Criteria:


The ohmmeter should read a low resistance in both directions. If the ohmmeter reads an infinite resistance, there may be an open circuit in the motor windings. Flag for review