Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Romex wet

User: codewarrior321, Location: 3 Hr 2 Min from Winged Horses

Asked on: Tuesday, March 8, 2011 at 1:40 pm EST
Answered on: Tuesday, May 14, 2024 at 2:29 am EDT

Question: Hi, I have a would be future customer call and ask me if it was ok for an electrician to pull the whole house without a roof, open to the elements. She told me that her electrician had pull all the romex cables in the house without a roof. She said that it has rained in the house for about 3 to 5 times that she can remember and that it had frozen over a couple of nights. So I told her that was not good that it was not legal. So I suggested to her to tell the electrician he would have to replace all the wiring in the house.Reason the insulation of the cable would absorb moisture, that would give her problems later, all connection or splices would have absorb moisture too.I tried to get something I could use from the code, the only thing I came up with was Listing and Labeling and article 334.Thanks for any comments

NEC Code Violations



Article 110.11

Electrical equipment shall be installed in a neat and workmanlike manner.


Article 300.4

Conduit and other raceways shall not be installed in wet locations unless installed in a manner specifically approved for such locations.

Article 334.12

Cable installed in wet locations shall be listed and labeled for such use.

Consequences of Exposure

Moisture absorption in cable insulation can lead to: Electrical shorts and ground faults Reduced insulation resistance and increased risk of shock or fire Corrosion of metal conductors and connectors Moisture absorption in splices and connections can: Damage the insulation and reduce electrical safety Compromise the integrity of the connection, leading to potential arcing or electrical faults Freezing temperatures can cause water absorbed in the insulation to expand, further damaging the insulation and potentially leading to failures.

Recommendations for Resolution:
The electrician should be required to replace all wiring that has been exposed to moisture. The new wiring should be listed and labeled for use in wet locations (e.g., UF cable). All splices and connections should be made using appropriate moisture-resistant materials and techniques.* The customer should consider consulting with a licensed electrician to inspect the installation and verify that it meets all applicable code requirements. Flag for review