Topic: Challenge question 2 in 2005 NEC prep book motor calcs.

User: electricalperson, Location: massachusetts

Asked on: Tuesday, March 8, 2011 at 5:46 pm EST
Answered on: Tuesday, May 14, 2024 at 2:30 am EDT

Question: The question states:The motor feeder conductor size for 3 15 hp 208v 3 phase motors, 3 3 HP 208v 1 phase motors and 3 1 HP, 120v 1 phase motors will be_____A 2/0 awg, B 3/0 AWG, C 4/0 AWG, D 250 MCM15 HP = Largest motor load. 46.2 x 1.25 = 57.75(46.2 x 1.25) + 46.2 + 46.2 + 18.7 + 18.7 + 18.7 + 16 + 16 +16 = 254.25250 MCM is rated for 255 ampsmy answer was D but the example in the books answer is Ci think the book is wrong since i have the answer key right infront of me and they only added in 1 1 HP motor.

The correct answer is C. 4/0 AWG.

To calculate the motor feeder conductor size, we need to determine the total full-load current (FLA) of all the motors.3 Phase Motors

FLA for 15 hp motor = 46.2 ampsTotal FLA = 3 46.2 = 138.6 amps

1 Phase Motors

FLA for 3 hp motor = 18.7 ampsFLA for 1 hp motor = 16 ampsTotal FLA = 3
18.7 + 3 * 16 = 89.4 amps

Total FLA

Total FLA = 138.6 + 89.4 = 228 ampsUsing the NEC Table 310.16, for a continuous load of 228 amps, the conductor size should be

4/0 AWG
.Therefore, the correct answer is C. 4/0 AWG. Flag for review