Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: On a motor, doing the Insulation test with a megger at 500 volts.

User: jonathn1, Location: Macau, China

Asked on: Wednesday, March 9, 2011 at 1:11 am EST
Answered on: Tuesday, May 14, 2024 at 2:32 am EDT

Question: Recently involved with testing insulation on transformers for a site in macau China. It was proposed that the test be completed by installing the black lead of the megger to the three phase wires and the red lead to the ground wire. Since we are testing insulation only and not the voltages i understand it doesnt really matter which location you place the leads. But as a matter of consistency and safety I was always trained to place the black lead on the ground wire and move the red lead to each phase. This would have me practice safe skills for when I was trying to get voltage readings later.Well they came back to me and said that they had a study done which showed placing the black lead on the power wire and the red on the ground created some type of boundary in the wire which gave a better result on the test.Have I been mis trained? Is this true? I figured the first place to check is with the people here I have learned to trust and see what i can find out.Any information on the correct procedure for testing i would certainly appreciate.

Correct Procedure for Insulation Resistance Testing of Transformers

The correct procedure for insulation resistance testing of transformers is to connect the black lead of the megger to the ground wire and the red lead to each phase wire, as follows: Ground Wire

Connect the black lead to the ground wire of the transformer.


Phase Wires

Connect the red lead to each of the three phase wires individually.

Rationale
Safety

Connecting the black lead to ground ensures that any potential surge or discharge will be directed to ground, minimizing the risk of harm to the tester or equipment.


Consistency

This method ensures consistency in testing results, regardless of the specific phase or transformer being tested.

Accuracy

While it is generally true that the location of the leads does not significantly affect insulation resistance measurements, there is no evidence to support the claim that switching the leads provides a "boundary" effect that improves accuracy.

Incorrect Method


Connecting the black lead to the phase wires and the red lead to the ground wire, as proposed in your case, is incorrect and could potentially be unsafe.

Additional Considerations
Ensure that all connections are secure and free of corrosion. Discharge the transformer before testing to prevent damage to the megger. Use a megger with an appropriate voltage rating for the transformer being tested.* Compare the measured insulation resistance values with the manufacturer's specifications or established standards.

Conclusion

You have been correctly trained to connect the black lead of the megger to the ground wire and the red lead to the phase wires for insulation resistance testing of transformers. The proposed method of connecting the leads is not accurate or recommended. Flag for review

Previous Question Next Question