Topic: Conductor Sizing for 2500 Amp MDP

User: CEBen, Location: Casper, Wyoming

Asked on: Wednesday, March 9, 2011 at 9:32 am EST
Answered on: Tuesday, May 14, 2024 at 2:32 am EDT

Question: We have an engineered job for a Residence Hall. The main breaker is outside next to the utility CT Section and is 2500 amps. The switchgear is fully rated. The MDP is 100' away and inside the building. The MDP is Main Lug Only. THe system is 4 wire grounded Y.The engineer has called out 6 sets of 600 kcmil THHN between the 2500 amp main breaker and the MDP. The inspector is calling for 6 sets of 750 kcmil THHN between the main breaker and the MDP.Accoridng to the inspector the engineer has sized the wire too small based on the rule in NEC Table 310.15(B)(2)(a) for 4-6 current carrying conductors.What is the proper wire size between the main 2500 amp breaker and teh MLO MDP to meet NEC 2009 Code?

Proper Wire Size

According to NEC Table 310.15(B)(2)(a), for four to six current-carrying conductors in raceway or cable, the ampacity must be reduced to 80% of the ampacity given in Table 310.15(B)(16), which is based on a single conductor in free air.

Size Reduction Calculation

For six conductors, the ampacity reduction factor is 0.80. Therefore, the ampacity of the 600 kcmil THHN conductors must be reduced to 0.80 * 500 amps = 400 amps.

Required Ampacity

The maximum demand of the Residence Hall is not provided in the question. However, assuming a maximum demand of 2500 amps to match the main breaker rating, each of the six conductors must be capable of carrying 2500 amps / 6 = 417 amps.

Conclusion

Based on the NEC requirements, the 600 kcmil THHN conductors are not sufficient to meet the ampacity requirements for this installation.

The proper wire size between the main 2500 amp breaker and the MLO MDP is 750 kcmil THHN.