User: mikeybmdb32, Location: Charlotte, NC
Asked on: Wednesday, March 9, 2011 at 11:20 am EST
Answered on: Tuesday, May 14, 2024 at 2:33 am EDT
Question: I recently visited a construction site where the contractor had removed the bolted metal cover for an existing, live 120/208V panel and replaced it with a cardboard cover that he had bolted in place. I really can't find anything in the NFPA70 or 70E which states that this is a violation of code, but it just doesn't seem right to me since cardboard doesn't provide the rigid protection that a metal cover can.Anyone know of a place in the code that forbids such a setup?
NFPA 70 (National Electrical Code) 110.26(A) requires electrical enclosures and raceways to be installed to provide appropriate protection against physical damage. 312.5(A) requires enclosures for overcurrent devices to be made of metal or other approved material.
NFPA 70E (Standard for Electrical Safety in the Workplace) 110.26(A) is incorporated by reference into NFPA 70E. 200.4(J) requires enclosures in electrical installations to be maintained in good condition, including the protection of live parts from physical damage.
Interpretation
The cardboard cover used by the contractor does not meet the requirements of NFPA 70 or 70E. Cardboard is not an approved material for electrical enclosures and does not provide adequate protection against physical damage. The use of a cardboard cover on a live electrical panel is a violation of code and poses a significant safety hazard.
Recommendation
The cardboard cover should be immediately replaced with a proper metal cover that meets the requirements of NFPA 70 and 70E. Flag for review