Topic: No Disconnect for AC, dwelling unit

User: Npstewart, Location: Logan, Utah

Asked on: Wednesday, March 9, 2011 at 11:23 am EST
Answered on: Tuesday, May 14, 2024 at 2:33 am EDT

Question: In a dwelling unit, is there any excuse for not having a disconnect for the AC?The Air handler is a vertical unit in a closet with the water heater. The water heater has no disconnect BUT it has a lockable breaker installed in the panel.The Air handler has NO disconnect, NO lockable breaker, and the panel is NOT located within site however it is relatively close (about 30 feet down the hall in a room)Thanks.

Generally speaking, all appliances should have a disconnect where they are located. If the AC is plugged into a receptacle, then the receptacle should be served by a disconnect. If the unit is hard wired, then it should have a disconnect switch or circuit breaker at the unit.NFPA 70 (National Electrical Code) 2020 Article 440.14 states, in part:"Disconnecting Means.Where one or more disconnecting means is required for motors rated over 1/2 horsepower, a single disconnecting means with a horsepower rating not less than that of the largest motor served shall be permitted where the disconnecting means is capable of simultaneously interrupting all of the conductors of the circuit."Since water heaters are not motors, NEC 440 would not apply. NEC 240.40(B) states, in part:"Disconnecting Means. Where required, the disconnecting means shall be installed at a readily accessible location in sight from the heater, or where the heater is so located that it is impractical to mount the disconnecting means in sight from the heater, the disconnecting means shall be installed at the nearest readily accessible location outside the heater room. ..."For the AC unit, a disconnect would be required at or near the unit itself. The circuit breaker in the panel would not suffice.For the water heater, a disconnect would be required at or near the unit itself or at the nearest readily accessible location outside the heater room. The lockable breaker in the panel would suffice. Flag for review

Previous Question Next Question