Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Fire pumps!

User: electricalperson, Location: massachusetts

Asked on: Wednesday, March 9, 2011 at 1:19 pm EST
Answered on: Tuesday, May 14, 2024 at 2:33 am EDT

Question: according to 695.6C2 , when sizing conductors for a fire pump motor we follow 430.22 and also follow the voltage drop rule of 695.7if i have a fire pump rated at 25hp 208v i would size that according to table 430.25074.8 x 1.25 = 93.5a so i would need a #3 awg conductorthe confusion sets in with article 695.7 voltage drop. in the example in the book it has a 25 hp 208v 3 phase fire pump motor located 175 feet away from the service. the controller is 150 feet away from the service.so the VD to the controller cant be more than 15 percent and the motor cant be more than 5% when operating at 115% full load current.so after all the math is done, i dont have any problem with the formula at all( cmil = (1.732 x k x LRC x D)/VD )after all the math is done i come up with a #3 to feed the controllerwhat i dont understand is the 115% part. in the next example we size conductors to the motor from the controller. he takes the FLC from table 430.250 and multiplies it by 1.15 instead of 1.25 so we come up with 86amps instead of the 93 amps using the 1.25 multiplier.the formula is cmil = (1.732 x 12.9 x 86 x 175)/10.4 (the 10.4v is 5% of 208v per 695.7)the answer is a #4 AWG conductor.the question is how come in the first example when sizing conductors to the motor we use 125% according to article 430.22 and when we sized the conductors from the controller to the motor we use 115% instead? i am very confused and i hope i did not confuse anyone else with this long thread.

The reason for the difference in the multiplier used when sizing conductors for a fire pump motor in accordance with NEC articles 430.22 and 695.7 is due to the way the motor will operate in the event of a fire. 430.22 applies to the sizing of conductors for fire pumps that are required to operate continuously for an extended period of time, such as during a fire. In this scenario, the motor will be operating at or near its full load current for a sustained period, so the conductors need to be sized accordingly to handle the increased current flow. Therefore, a multiplier of 1.25 is used to account for this continuous operation. 695.7 applies to the sizing of conductors for fire pumps that are intended to operate for a limited duration, such as during the initial stages of a fire when the water pressure needs to be quickly increased. In this scenario, the motor will typically operate at a higher than normal current for a short period of time, but it is not expected to operate continuously at this higher current level. Therefore, a multiplier of 1.15 is used to account for this intermittent operation.It is important to note that both articles 430.22 and 695.7 require that the conductors be sized to handle the voltage drop requirements specified in the respective articles. In the example you provided, the voltage drop to the controller cannot exceed 15%, and the voltage drop to the motor cannot exceed 5%. These voltage drop requirements ensure that the motor will receive sufficient voltage to operate properly, even during the most demanding conditions.By using the appropriate multiplier and voltage drop requirements for the specific application, you can ensure that the conductors for a fire pump motor are properly sized to handle the expected current flow and voltage drop conditions. Flag for review

Previous Question Next Question