User: Mr 3phase
Asked on: Wednesday, March 9, 2011 at 1:28 pm EST
Answered on: Tuesday, May 14, 2024 at 2:33 am EDT
Question: I recently priced out a project to install harwired smoke detectors in the front stair well of a four story, three family dwelling in Boston. The top two floors are a combined unit. The rear stairwells were already hardwired, and had to be tied into the front throught the basement. Can NM be used legally (fished through the walls and ceiling), passing from one floor to another? Seems that the Mass code amendment leads me to beleive that it can't be used, and must be piped. Anyone?
Massachusetts Electrical Code (527 CMR 12)527 CMR 12.10.
4.1 states that "Nonmetallic-sheathed cable shall not be used as a penetration barrier between floors of a building."Interpretation
Based on this code amendment, it is not permissible to use NM cable to pass from one floor to another in a multi-story building in Massachusetts. All cables passing between floors must be installed in conduit or other approved raceways.
Therefore, the answer to your question is no, NM cable cannot be used legally for this purpose.Alternative Options
Instead of using NM cable, you should consider using one of the following alternative options:
Conduit
Install the cables in EMT or PVC conduit. This provides a protective barrier against fire and physical damage.
Mineral-insulated cable (MIC)
MIC is a type of cable that has a mineral insulation and a metal sheath. It is fire-resistant and can be installed without conduit.*
Fire-rated cable
This type of cable is designed to withstand high temperatures and can be used in place of conduit.
Note: It is always advisable to consult with a qualified electrician to ensure compliance with all applicable codes and regulations. Flag for review