User: KHall, Location: Logan, Utah
Asked on: Wednesday, March 9, 2011 at 5:19 pm EST
Answered on: Tuesday, May 14, 2024 at 2:34 am EDT
Question: I just started renovations on an existing building. The main service switch is a 400A, 3P disconnect switch fused at 400A. Off the load side of the switch there are two sets of 2/0 THHN copper per phase. One set of 2/0 runs about 15 feet thru a wireway and terminates in a 200A main circuit breaker protecting a lighting panel. The second set of 2/0 run about 10 feet into the wireway where they are each tapped with (2) #4 THHN copper conductors. Then the two sets of #4 terminate in a 100A,3P disconnect switch which is fused at 100A. This second set, with the 2/0 being tapped by the #4 just doesn't seem right to me. I have read art. 240.21(B) and I can't quite determine if or what it specifically violates. Any help would be appreciated!
Violation of NEC Article 240.21(B)
Article 240.21(B) of the National Electrical Code (NEC) states that "Overcurrent protection for conductors tapped from feeders shall be provided in accordance with the following:"* Conductors Tapped from Feeders with a Rating of 900 Volts or Less
Overcurrent protection for conductors tapped from feeders rated 900 volts or less shall be provided in accordance with 240.21(B)(1) through (B)(4).In this case, the feeder is rated at 400 volts and the tapped conductors are #4 THHN copper, which is rated for 90 volts. Therefore, the overcurrent protection requirements of 240.21(B)(1) through (B)(4) apply.
Specific Violation
Subsection (B)(2) of 240.21 states that:>
(B)(2) Taps from Feeder with Overcurrent Protection Rated 600 Amps or Less. Conductors tapped from feeders with overcurrent protection rated 600 amperes or less shall have overcurrent protection not exceeding the ampacity of the tap conductors in accordance with 310.15(C)(1).The overcurrent protection for the tapped conductors (#4 THHN) is the 100A fuses in the disconnect switch. However, the ampacity of the tapped conductors is only 70A, according to Table 310.15(C)(1). Therefore, the 100A fuses exceed the ampacity of the tapped conductors, which is a violation of 240.21(B)(2).
Resolution:
To correct the violation, the 100A fuses in the disconnect switch must be replaced with fuses rated at 70A or less. Flag for review