Topic: Nec 240.4

User: erickench, Location: Brooklyn, NY

Asked on: Wednesday, March 9, 2011 at 6:08 pm EST
Answered on: Tuesday, May 14, 2024 at 2:35 am EDT

Question: Was teaching a seminar today and the question came up. Let's suppose you have a motor circuit with 18A which includes the 125% factor flowing through it. According to NEC table 310.16 the ampacity of No. 14 AWG is 20A at 75'C. However, NEC 240.4(D)(2) state's that 14 AWG must be protected at 15A. According to 240.4(B) the next higher standard OCPD is permitted to be used under certain conditions. We have 18A flowing through the circuit so the next higher OCPD rating would be 20A.Can we use a 20A OCPD for a No. 14 AWG at 75'C for this motor circuit?

Yes, under these specific conditions, you can use a 20A OCPD for a No. 14 AWG at 75'C for this motor circuit.

Explanation: NEC Table 310.16 specifies the ampacity of No. 14 AWG copper wire at 20A under normal conditions (75°C). However, NEC 240.4(D)(2) states that No. 14 AWG wire must be protected at 15A when used in circuits not covered by NEC 210.8(A). NEC 240.4(B) allows the use of the next higher standard OCPD rating (20A in this case) under certain conditions: The actual load does not exceed the ampacity of the wire (18A in this case is within the 20A ampacity of No. 14 AWG).* The next higher OCPD rating (20A) is standard equipment for the application.In a motor circuit, the 125% factor is applied to account for the inrush current of the motor. The actual load current (18A) is within the ampacity of No. 14 AWG, and 20A OCPDs are standard equipment for motor applications.Therefore, it is permitted to use a 20A OCPD for a No. 14 AWG at 75°C in this motor circuit, despite the 15A protection requirement for NEC 240.4(D)(2). Flag for review

Previous Question Next Question