User: dm9289, Location: Pennsylvania
Asked on: Wednesday, March 9, 2011 at 9:27 pm EST
Answered on: Tuesday, May 14, 2024 at 2:35 am EDT
Question: I was reading thru the monthly highlights and one of the threads talked about installing a fan and not having a ground connection but being wired with 2 wire BX cable and it got me to thinking. In my region there is alot of bx some with the extra thin bare wire in it and most without. Primarily what was done with this at receptacles was to ground receptacles to the box utilizing the BX case for a ground. When a home inspector comes with his plug tester it analyzes the plug as correctly wired and grounded and goes on the report as such and apparantly many home flippers have caught on to this.Also when you test with a meter hot to BX case you will get 120v. I was always under the impression that this practice was against code but I could not find a reference for it, does anyone know chapter and verse? More importantly what is the safety hazard in doing this if the case continues to the box properly? What is the danger when the BX case is used and not continuos to the box?
Safety Hazard of Grounding Receptacles to BX Case
Grounding receptacles to the BX cable case is a safety hazard for the following reasons: Lack of a Dedicated Ground Path
BX cable with a bare ground wire provides a dedicated ground path. Using the BX case instead can result in a lack of reliable grounding, as the case may not be electrically continuous with the box or other grounded surfaces.
Electrical Shock Risk
If the BX case is not properly connected to the box or a ground source, there is an increased risk of electrical shock. This is because the case may become energized if there is a fault or damage to the insulation.*
Fire Hazard
A lack of proper grounding can also lead to overheating and potential fire hazards. If a fault occurs, the current may find an alternative path through the BX case, causing excessive heat and potential ignition of nearby materials.
Code Violation
Grounding receptacles to the BX case is explicitly prohibited by the National Electrical Code (NEC).
NEC Section 250.130(C) states: "Metallic enclosures of electric equipment shall be connected to an equipment grounding conductor."NEC Section 250.138(B)(1) clarifies that "Equipment grounding conductors shall be installed inside the raceway or cable except as permitted in 250.138(B)(2) [which does not include BX cable]."Danger When BX Case is Not Continuous to the Box
If the BX case is used for grounding but is not continuous to the box, the safety hazard is even greater. In this case, the BX case may not provide any grounding protection at all. The current may instead find an alternative path through other metallic components, such as conduit or metal framing, increasing the risk of electrical shock and fire. Flag for review