Question: I?m currently removing equipment in a Telco Central office. We use -48v power feeds with an integrated ground plane. My question is I need to lead verify the grounds to make sure that they where installed correctly so I don?t knock out service to a working system. I get .02mV with a VOM if I use a Clamp on amp meter will it do me any good to help verify the correct leads? The equipment to be removed has been fuse down so on the -48V leads I get 0V with my VOM. Please help I don?t want to get fired!!

Using a Clamp-On Amp Meter to Verify Ground Leads

While a clamp-on amp meter can measure AC current, it cannot be used to verify the correctness of ground leads in a -48V DC system.

Clamp-On Amp Meter Limitations

Clamp-on amp meters measure AC current, not DC current. They can induce a small amount of AC current when clamped around a conductor, but this is not a reliable indicator of the quality of a DC ground lead.

Ground Lead Verification Method


To verify the correctness of ground leads in a -48V DC system, follow this procedure:1. Safety Precautions

Ensure that all equipment is properly grounded and that power is disconnected before performing any work.2.

Locate Ground Reference Point

Identify the main grounding bus or bar in the central office where all ground connections should be terminated.3.

Use a Digital Multimeter (DMM)

Set the DMM to the millivolt (mV) range.4.

Connect DMM Leads

Connect the positive lead of the DMM to the ground reference point.5.

Measure Ground Leads

Connect the negative lead of the DMM to each ground lead to be verified.6.

Verify Readings

A correct ground lead should read close to 0mV (typically within a few millivolts).7.

Inspect Fuse

Check that the fuse on the -48V feed has not been blown. If it has, replace it with a new fuse of the same rating.8.

Rectify Faulty Leads

If any ground lead reads significantly higher than 0mV, it may indicate a loose connection or improper termination. Rectify the issue by tightening connections and/or re-terminating the lead as necessary.

Additional Tips:
Wear proper personal protective equipment (PPE) when working with electrical equipment. Use caution when working with high-voltage power. Document your findings and any corrective actions taken. If you encounter any difficulties or uncertainties, consult with a qualified electrician or engineer. Flag for review