User: lmtis, Location: Logan, Utah
Asked on: Thursday, March 10, 2011 at 8:48 am EST
Answered on: Tuesday, May 14, 2024 at 2:35 am EDT
Question: This Is a outside concrete tank with metal railling around the tank. There are motor starter saftey switches attached to metal strut and the strut is attached to the railling. The conduit feeding the enclouser has a ground conductor in the conduit and that ground is attached to the ground lug. Is the railling considered grounded under 250.136 (A) 2008 NEC
Yes, the railing is considered grounded under 250.136 (A) of the 2008 NEC.
250.136 (A) states that "Metal raceways, cable trays, cablebus, and other metal enclosures for conductors shall be grounded unless exempted by 250.136(B)."The railing in this case is a metal enclosure for conductors, and it is not exempted by 250.136(B). Therefore, it must be grounded.The fact that the ground conductor in the conduit is attached to the ground lug does not change this requirement. The ground conductor is only there to provide a path for fault current to flow back to the source. It does not provide a ground reference for the railing.The railing must be grounded separately from the conduit. This can be done by bonding the railing to a grounding electrode system (GES) or by using a grounding electrode conductor (GEC) to connect the railing to a GES. Flag for review