User: navyman, Location: Lehigh county,PA
Asked on: Thursday, March 10, 2011 at 2:32 pm EST
Answered on: Tuesday, May 14, 2024 at 2:37 am EDT
Question: I took the pennsylvania journeyman exam a few weeks ago and missed passing by one point. I have been studying using Mike's material for weeks and am going to take it again very soon. However...I cannot find the answer to a question that was on the test.....question is.....The zone classification for hazardous locations is determined by whom?a. qualified personb. master electricianc. person with jurisdictionthose are the only choices i remember. is this in the code book? I have the 2011 code and realize the test pertains to the 2008 book.
The correct answer is c. person with jurisdiction.
NEC 500.5(A) states that "The person having jurisdiction shall determine the classification of all hazardous (classified) locations." Flag for review