User: DaveBowden, Location: St Petersburg FL
Asked on: Thursday, March 10, 2011 at 3:20 pm EST
Answered on: Tuesday, May 14, 2024 at 2:37 am EDT
Question: Can anyone help me understand why an air handler with a 4.6kw heat strip and a blower motor with a 4.3 amp FLA would need a circuit with a minimum ampacity of 32.5 amps and a 35 amp breaker?The 2 story addition we just roughed in called for a 5kw heat strip in the air handler and we fed it with 10/2 romex (like we always do for a 5kw load). Now we get to go back and replace the 10/2 with 8/2. I'm not too happy about it, but I can't see any way around it other than trying to get the AC guy to change the stick on label with the requirements on it.
The minimum ampacity and breaker size are determined by NEC (National Electrical Code) requirements, which are based on safety considerations and to prevent overheating of wires and equipment. Here's a breakdown of the calculations
1. Circuit Ampacity (Minimum 32.5 Amps):
The 4.6kW heat strip requires 4.6 kW / 240 V = 19.2 Amps. The 4.3 Amp blower motor adds to the load, bringing the total to 19.2 Amps + 4.3 Amps = 23.5 Amps. NEC requires a minimum circuit ampacity of 125% of the total load, so 23.5 Amps x 1.25 = 29.4 Amps. The nearest standard ampacity rating above 29.4 Amps is 32.5 Amps.2. Breaker Size (Minimum 35 Amps)
NEC requires a circuit breaker to be sized at or above the circuit ampacity. Therefore, a
35 Amp breaker is required, as it is the nearest standard size above 32.5 Amps.
Use of 10/2 Romex
10/2 Romex is rated for a maximum ampacity of
30 Amps. Since the minimum circuit ampacity required is 32.5 Amps, 10/2 Romex is not sufficient to safely carry the load.
Replacement with 8/2 Romex
8/2 Romex is rated for a maximum ampacity of
40 Amps. This is within the required ampacity range (32.5 Amps minimum).
Conclusion:
Based on NEC requirements, a circuit with a minimum ampacity of 32.5 Amps and a 35 Amp breaker is necessary for the specified air handler. Using 10/2 Romex would violate code, so the circuit must be replaced with 8/2 Romex to ensure safety. Flag for review