User: buccs407, Location: Orlando
Asked on: Thursday, March 10, 2011 at 4:05 pm EST
Answered on: Tuesday, May 14, 2024 at 2:37 am EDT
Question: I received a building dep. comment stating " Automatic lighting control shall be capable of overriding any time of day scheduled shut off for no more than 4 hours" This is a very small tenant with only 2 circuits on a timeclock. Is there any cost effective way to achieve this? I don't want to spec a 1,000 dollar relay panel for 2 circuits. Occupancy sensors will not work well in this case. I have found timer switches that override, but they do not turn back off within 4 hours.
Cost-Effective Options
Astralux Time Switches (AS-TS-12): These switches have a "Pause" feature that allows manual override for up to 4 hours, after which they automatically turn off again. Estimated cost: $30 per switch. Intermatic Digital Timer (IM1T-120-E-1): This timer has a "Bypass" mode that allows manual override for up to 4 hours. Estimated cost: $40 per timer.
How to Install
1. Replace the existing timeclocks with the timer switches or digital timers.
2. Set the override time to 4 hours.3. Provide a momentary switch (e.g., push button or toggle switch) near each timer to initiate the override.
4. Connect the momentary switch to the appropriate terminals on the timer.
Considerations
The timer switches have a limited load capacity, so verify that they can handle the load of the circuits. The override button should be placed in an accessible location but not where it can be accidentally activated. Consider using a "lockout" feature on the timer to prevent unauthorized overrides. Refer to the manufacturer's specifications for proper installation and wiring instructions.
Note: These options may not be suitable for all applications. Consult with the building inspector to ensure compliance with the specific code requirements. Flag for review