Question: We are designing a commercial kitchen and in the past we would provide GFCI outlets above the counters for all convenant 120v outlets. I need to confirm somthing, has the code changed to where all 120v 20amp outlets even those that feed equipment within the kichen require GFCI protection?
Yes, the code has changed. As of the 2020 National Electrical Code (NEC), all 120-volt, 20-amp outlets in commercial kitchens are required to be GFCI-protected. This includes outlets that feed equipment within the kitchen.
NEC Section 406.4(D)(2)(b) states:> "All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the following locations shall have ground-fault circuit-interrupter protection for personnel:"> "...(2) Commercial kitchens"Exception
GFCI protection is not required for outlets that are part of a listed kitchen appliance that has integral ground-fault current protection provided by the manufacturer.
Reason for the Change:
The NEC change was made to enhance safety in commercial kitchens, where water and electricity are often present. GFCIs help protect against electrical shocks by interrupting the power supply when a ground fault occurs. Flag for review