User: lile001, Location: Midwest
Asked on: Thursday, March 10, 2011 at 8:54 pm EST
Answered on: Tuesday, May 14, 2024 at 2:38 am EDT
Question: Attached is a photo of a ground lug on a solar panel. This installer is going around installing dozens of them like this, and the inspectors don't mind at all since they've never seen solar panels before anyway and don't know better. Here is the setup:Aluminum solar panel frames are mounted on a galvanized steel frame. There is no aluminum mounting rail nor WEEB. As galvanized steel is not a decent conductor, the installer has added a copper ground wire, using the type of lug shown in the picture. The lug is attached with a self-tapping screw, but I could not tell if it was a galvanized steel or stainless steel self-tapping screw. It looks like a bugle head (cone head) screw, with no toothed lock washer underneath it. The lug looks like it is listed for CU-AL. This ground connection is accessible from the bottom, as it is a grade-mounted array, so it could presumably be removed if a panel was being serviced by removing the self-tapping screw. I suppose this satisfies 690.4(C) which requires that removal of a panel does not interrupt the ground for another panel. If this was a roof mounted array I don't see how it would comply. The installer used Noalox goo on the copper wire, I suppose to keep the copper and nearby aluminum from corroding. Will that wash off in the rain? Does it even work on copper?OK, let's see how many things we can find wrong with this grounding installation? I think there are several but I'd like to get some other opinions.What could be changed to make it right?
Grounding Issues
No aluminum mounting rail or WEEB
The lack of a conductive mounting rail or WEEB creates a potential discontinuity in the grounding path.
Galvanized steel frame is not a decent conductor
Galvanized steel has limited conductivity, reducing the effectiveness of the grounding connection.
Self-tapping screw may not be corrosion-resistant
If the self-tapping screw is galvanized steel, it may corrode in the presence of moisture and aluminum, weakening the connection.
Lug may not be suitable for the application
The lug appears to be listed for CU-AL but may not be designed for use in a wet or outdoor environment without additional protection.
Noalox paste may not be effective on copper
Noalox paste is primarily used to prevent corrosion between aluminum and steel, and its effectiveness on copper is questionable.
Code Violations
690.4(C)
Removal of a panel could interrupt the grounding path for other panels, as the ground lug is attached with a single self-tapping screw.
705.12(A)(3)
Grounding conductors must be protected against damage, which may not be the case for the exposed copper wire.
Improvements to Correct Issues: Use an aluminum mounting rail or WEEB to ensure a conductive grounding path. Use a corrosion-resistant self-tapping screw, such as stainless steel, to attach the ground lug. Mount the ground lug more securely, such as with a bolt or threaded stud. Use a grounding lug specifically designed for exposed outdoor applications. Apply a corrosion-resistant coating to the copper wire, such as heat shrink or a conductive paint.* Consider using a combination of aluminum and copper grounding conductors to minimize galvanic corrosion between different metals. Flag for review