Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: ground mount solar photovoltaics and cable trays

User: ocoee, Location: Golden Co

Asked on: Thursday, March 10, 2011 at 11:17 pm EST
Answered on: Tuesday, May 14, 2024 at 2:39 am EDT

Question: We are currently in the design process for large photovoltaic array. I have done several installations similar to this one. Usually we go underground with the "combined" DC source circuits. The system owner is has a strong personality and would like us to do all above ground wire management. We can do conduit but it has many challenges both from a installation standpoint, as well as cost and long term efficiency. I saw a picture of a ground mount system done with a cable tray type product called cable snake. They were routing several # 10 use-2 sunlight resistant single conductors. Looking at NEC 392-10 B1a requires a minimum of 1/0 for single conductors. What am missing? Also what class of cable is use-2 because I do not see where it is a approved method according to this article.It seems like it should be a approved method given that running DC source circuits under the array is accepted. IE interconnection between modules require no more than a clip or zip ties.Fyi The entire array is behind a fence and accessible to only qualified personal.thanks for your input.

NEC Requirements for Underground DC Source Circuits

NEC 690.31(B)(1)(a) requires that DC source circuits be installed underground or in a raceway that is embedded in concrete. The exception to this rule is for single conductors larger than 1/0 AWG, which can be installed above ground in accordance with NEC 770.

NEC Requirements for Overhead DC Source Circuits

NEC 690.31(D) allows DC source circuits to be installed overhead if they meet certain requirements, including: The conductors must be supported by a messenger wire or other approved means. The conductors must be protected from physical damage and contact with other surfaces.* The conductors must be spaced apart to prevent arcing.

Use of Cable Trays for DC Source Circuits

Cable trays are not specifically mentioned in NEC 690 for use with DC source circuits. However, they can be used to support and protect conductors if they meet the requirements of NEC 690.31(D).

Use of USE-2 Cable

USE-2 cable is a sunlight-resistant, outdoor-rated cable that is commonly used for photovoltaic applications. It is not a type of cable specifically recognized in NEC 690. However, it can be used for DC source circuits if it meets the requirements of NEC 690.31(D) and is installed in a manner that ensures its protection from physical damage and contact with other surfaces.

Conclusion

Although NEC 690 does not specifically mention the use of cable trays or USE-2 cable for DC source circuits, it is possible to use them if they meet the general requirements of NEC 690.31(D). The primary concern is to ensure the conductors are adequately supported, protected from physical damage, and spaced apart to prevent arcing.It is important to note that the NEC is only a minimum standard, and stricter requirements may be imposed by local authorities or the system owner. It is always advisable to consult with local authorities and the system owner before designing and installing a photovoltaic system. Flag for review

Previous Question Next Question