User: jcole, Location: Lawrenceburg, Kentucky
Asked on: Friday, March 11, 2011 at 6:55 am EST
Answered on: Tuesday, May 14, 2024 at 2:39 am EDT
Question: Hello Guys and Gals.One of our departments recently moved to a multifloor building that have other tenants on the upper floors not associated with us. They had their own phone sytem installed by our communications dept. He said he needed wire connected to building ground. I assumed he meant grounding electrode system.I installed a 10awg stranded wire to nearest building steel with a listed device.Is there anything wrong with this installation per NEC or anyother code that may govern this? I my opinion, 800.100B(2)2 allows this.What is meant by intersystem bonding termination per 800.100B(2)Thanks for replies.
NEC Compliance
Your installation appears to comply with the NEC. Section 800.100(B)(2)2 states that "the intersystem bonding termination shall be connected to the grounding electrode system as close as practicable to the service equipment."In your case, you have connected the wire to the nearest building steel, which is typically an acceptable grounding electrode. The use of a listed device is also in accordance with the NEC.
Intersystem Bonding Termination
The intersystem bonding termination is the point where the grounding systems of different services or systems are connected to each other. This is done to equalize the electrical potential between the different systems and prevent dangerous voltage differences.In the context of your installation, the intersystem bonding termination would be the point where the wire from the phone system is connected to the grounding electrode system.
Additional Considerations
While your installation is likely code-compliant, it's always a good idea to check with the local building or electrical inspector for specific requirements in your area.Additionally, it's important to note that the grounding requirements of telecommunications systems may differ from those of electrical power systems. Consult with the phone system manufacturer or an electrician specializing in telecommunications for any specific grounding requirements. Flag for review