Question: can i pull the feed wires to 5 vfd's and the outgoing power in the same conduit providing the conduit is large enough of course.
Yes, you can pull the feed wires to 5 VFDs and the outgoing power in the same conduit, provided that the conduit is large enough to accommodate all of the wires and that the wires are properly installed.Here are some things to keep in mind when pulling wires in a conduit: Conduit size
The conduit must be large enough to accommodate all of the wires without overcrowding. The National Electrical Code (NEC) requires that conduits be filled to no more than 40% of their capacity. For example, a 1-inch conduit can accommodate up to 12 AWG wires.
Wire type
The wires must be rated for the voltage and current that will be flowing through them. The NEC requires that wires be sized according to their ampacity. For example, a 14 AWG wire can handle up to 15 amps.*
Wire installation: The wires must be properly installed in the conduit. The wires should be pulled through the conduit without kinks or bends. The wires should also be secured to the conduit at regular intervals.If you are not sure whether or not the conduit is large enough or if the wires are properly installed, it is best to consult with a qualified electrician. Flag for review