User: eadd9000, Location: Eastern Oregon
Asked on: Friday, March 11, 2011 at 8:57 am EST
Answered on: Tuesday, May 14, 2024 at 2:39 am EDT
Question: Our mcc panel at our facility had degraded to the point that it needed to be replaced.we are running 5 motors of the starters in the mcc panel i intend to replace the panel with vfd's that being said i was going to run a 2 inch conduit from the main breaker box to a wireway ( total run of pipe 60' ) pull in my 24 # 12 awg conductorsthree hots and a ground for each vfd then i would like to pull another 24 #12 awg conductors through the same conduit out of the vfd's to run the motors.two questions do i need to pull a ground for each vfd and is pulling the incoming and outgoing power through the same conduit a bad idea.i called ac tech and they said i might get some noise on the line but it should be fine but i just wanted to double check with you guys.p.s. i'm a newbiesorry if i insult anyones intelligence and thank you mike holt your books got me to the point where i can proudly tell my dad i'm a master electrician.
Grounding
Yes, you need to pull a ground wire for each VFD. The ground wire provides a path for fault current to flow back to the source, protecting equipment and personnel from electrical shocks.
Incoming and Outgoing Power in the Same Conduit
It is generally not a good idea to pull incoming and outgoing power through the same conduit. This can create potential interference between the two circuits, leading to noise and other issues. Additionally, in the event of a fault, the current flowing through the conduit could damage the incoming power cables.
Recommendations
Run separate conduits for the incoming and outgoing power cables. Use shielded cables for the incoming power lines to minimize interference. Ground each VFD separately.
Other Considerations: Make sure the conduit is adequately sized for the number and size of conductors being pulled through. Use a conduit body or pull box to facilitate the pulling of the wires. Label the conduits clearly to avoid confusion during installation and maintenance. Flag for review