Topic: Metering 4 wire 240 3ph open delta

User: mclark, Location: Brooklyn, NY

Asked on: Friday, March 11, 2011 at 9:00 am EST
Answered on: Tuesday, May 14, 2024 at 2:39 am EDT

Question: The newer solid state POCO polyphase meter ( Landis&Gyr kbase S4 series AXS4e) reads the 3 phases as Phase A 0deg Phase B 180deg and Phase C (high leg) 270deg for Phase Voltages, then reads phase currents with phase angles corresponding - for example Ia 37deg Ib 215deg Ic 305deg yielding somewhere approx 0.8xx power factor each phase in my opinion. from Cos(37-0) Cos (215-180) Cos (305-270).But how do we sum these to obtain the actual billed kWh? Why the orthogonal angles rather than 120deg?Although this small general service does not have demand nor power fastor charges - we are trying to ballance the loads, apply power factor correction if needed to sub panels, and minimized billable kWH. The idea of investing in power factor and balance being that a closer to unity balanced system is easier to drive by a small sized standy generator even if the POCO does not charge power factor penalty.In trying to manage the loading and relate the work we are doing to actual billable kWh we are reading the meter several times a day and logging that data - I am just having a hard time relating our "in the field" true rms power probe readings to the accumulated digitially integrated meter readings. Can convert the vars to watts with the Cos(angles) as above but how does that L&G meter vector sum 0deg, 180deg and 270deg for billable kWh?!

Meter Phase Readings and Angles

The POCO polyphase meter uses orthogonal angles (0°, 180°, 270°) for phase measurements because it simplifies the vector summation process for polyphase power calculations.

Power Factor Calculation

The power factor (PF) for each phase can be calculated using the cosine of the phase angle difference between the voltage and current:

PF = cos(Phase Angle Difference)
For example, with Phase A voltage at 0° and Phase A current at 37°, the power factor would be:
PF = cos(37° - 0°) = 0.809
Vector Summation for kWh

To calculate the total kWh, the meter vectorially sums the power (VI) of each phase. The orthogonal angles simplify this process: Phase A: Power = VA PF = VA 0.809 Phase B: Power = VB PF = VB 0.809 Phase C: Power = VC PF = VC 0.809The total power (P) is the vector sum of these three phase powers:
P = PA + PB + PC
Since all three phase powers have the same power factor, the total power factor (PF) is also 0.809:
PF = P / (VA + VB + VC) = 0.809
Relating Field Readings to Meter Data

To relate your field power probe readings to the accumulated meter readings:
Measure the true RMS voltage and current for each phase. Calculate the power factor for each phase using the phase angle difference. Multiply the voltage and current by the power factor to obtain the power for each phase. Sum the power of each phase to get the total power. The ratio of the calculated total power to the logged meter data will provide an estimate of the accuracy of your field readings.

Note: The 270° angle for Phase C (high leg) is due to the higher voltage on that phase in a wye-connected system. Demand and power factor charges are typically only applied to commercial and industrial customers with larger loads.* Balancing the loads and improving power factor can reduce system losses and improve generator efficiency. Flag for review