Question: Our mcc panel at our facility had degraded to the point that it needed to be replaced.we are running 5 motors of the starters in the mcc panel i intend to replace the panel with vfd's that being said i was going to run a 2 inch conduit from the main breaker box to a wireway ( total run of pipe 60' ) pull in my 24 # 12 awg conductorsthree hots and a ground for each vfd then i would like to pull another 24 #12 awg conductors through the same conduit out of the vfd's to run the motors.two questions do i need to pull a ground for each vfd and is pulling the incoming and outgoing power through the same conduit a bad idea.i called ac tech and they said i might get some noise on the line but it should be fine but i just wanted to double check with you guys.p.s. i'm a newbiesorry if i insult anyones intelligence and thank you mike holt your books got me to the point where i can proudly tell my dad i'm a master electrician.

1. Do you need to pull a ground for each VFD?

Yes, you should pull a separate grounding conductor for each VFD. Although the conduit will provide a path for the ground current, it is not considered a suitable grounding conductor.2. Is pulling the incoming and outgoing power through the same conduit a bad idea?

No, it is not necessarily a bad idea to pull the incoming and outgoing power through the same conduit, as long as you follow these guidelines: Use flexible metal conduit (FMC) or intermediate metal conduit (IMC) rated for the voltage and current of the circuit. Keep the incoming and outgoing conductors separated by at least 6 inches (150 mm). Use conduit bodies or junction boxes to maintain separation between the two sets of conductors at entry and exit points.

Additional Considerations



Conduit Fill

Ensure that the conduit is not filled to more than 40% of its capacity.

Electromagnetic Interference (EMI)

Pulling the incoming and outgoing power through the same conduit can create EMI, which may interfere with the operation of the VFDs. Consider using shielded cables or implementing other EMI mitigation techniques to reduce interference.


Insulation

The conductors should be properly insulated and rated for the voltage and temperature of the circuit.*

Future Expansion:
Consider leaving some spare conduit capacity for future expansion or additional circuits.Overall, replacing the MCC panel with VFDs and running the power conductors through a shared conduit can be a viable solution. However, it is crucial to follow proper electrical practices, including providing a separate grounding conductor for each VFD and maintaining separation between the incoming and outgoing conductors. Flag for review