Question: I am trying to find out if type AC cable is listed for passing thru fire rated wallsI have searched articles 300.21 for fire spread and 320 for type AC cable.I noticed that 320 reference UL listing 1685 for AC cable as being listed as low smoke and flame spread.where can I can information on wiring methods listed for fire rated wall floors etc?am I correct in reading article 320 as type AC cable is listed for use as an approved wiring method for article 517 Patient rooms.Thanks.Cameron
Wiring Methods for Fire-Rated Walls and Floors
The information on wiring methods listed for fire-rated walls and floors can be found in Article 300 of the National Electrical Code (NEC).
Article 300.21: Fire Spread
This article prohibits the passage of cables or raceways through fire-rated walls or partitions unless they are installed in accordance with specific requirements to prevent the spread of fire.
Article 320: Type AC Cable
Article 320 addresses the use of Type AC cable. It references UL Listing 1685, which certifies that Type AC cable meets the requirements for low smoke and flame spread.
Article 517: Patient Care Spaces
Article 517 contains specific requirements for electrical installations in patient care spaces, including patient rooms. However, it does not explicitly address Type AC cable.
Conclusion
Based on the information provided in the NEC, Type AC cable is not specifically listed for use in fire-rated walls or floors. However, it is listed for low smoke and flame spread, which may make it suitable for certain applications where fire protection is a concern.To determine the specific requirements for wiring methods in fire-rated walls and floors, refer to Article 300 of the NEC and consult with a qualified electrician. Flag for review