User: larrybartowski, Location: Northern illinois
Asked on: Friday, March 11, 2011 at 11:14 am EST
Answered on: Tuesday, May 14, 2024 at 2:40 am EDT
Question: I'm far from an expert on classified locations so I could use some help. I am bidding a job in MN. There is a note on the riser that reads that all wiring methods must conform with class 1 division 2 locations. The building has a shop, a warehouse, and some office space. I've been reading through code articles on hazardous locations....but I have questions:1. If the entire building is class 1, div 2 then would that mean that no seals are required because the conduits won't be entering into any non-classified locations?2. Do the fixtures need to be explosionproof?If the entire building is of this classification it seems to me that everything needs to be in rigid, even in the office space, with cord drops to each high bay fixture in the warehouse?
1. Seals
If the entire building is classified as Class 1, Division 2, then it is considered a single hazardous location. In this case, seals would not be required for conduits entering or leaving the building, as they are not transitioning between classified and non-classified locations.2. Fixtures
Yes, all fixtures in a Class 1, Division 2 location must be explosionproof. This is because they have the potential to produce sparks or heat that could ignite hazardous vapors or gases.3. Conduit Requirements
Based on the classification, the following conduit requirements apply: Shop and Warehouse (Exposed Locations)
Rigid metal conduit (RMC), intermediate metal conduit (IMC), or electrical metallic tubing (EMT) must be used.
Office Space (Concealed Locations)
EMT or non-metallic conduit (NMC) can be used.
High Bay Fixtures
Cord drops are typically used for high bay fixtures in warehouses. The cord and its supporting means must be rated for the hazardous location.
Additional Considerations Ventilation
Proper ventilation is essential to reduce the accumulation of hazardous vapors and gases.
Grounding
Grounding must be adequately installed to minimize the risk of static discharge.
Electrical Equipment
All electrical equipment must be suitable for use in Class 1, Division 2 locations.*
Wiring Methods: Wiring methods must conform to the requirements of the National Electrical Code (NEC) for hazardous locations.It is important to note that these are general guidelines. The specific requirements may vary depending on the specific hazards present in the location. It is always advisable to consult with a qualified electrical engineer or inspector for guidance on the design and installation of electrical systems in hazardous locations. Flag for review