User: mityeltu, Location: Tennessee
Asked on: Friday, March 11, 2011 at 1:56 pm EST
Answered on: Tuesday, May 14, 2024 at 2:41 am EDT
Question: I was told by a colleague that there is an IEEE standard that deals with heat trace and divisional power.I was told that this standard indicated that 1E equipment did not necessarily have to be powered from 1E power. The example that was apparently used in the standard was the RWST (Refuelling Water Storage Tank). According to my source, this standard says that because of the nature of 1E power and heat trace that the use of heat trace on the RWST did not require divisional power because after an accident, like say a LB LOCA, the time between the break and the full use of the RWST will be such that the tank will be empty long before the loss of the heat trace has any effect.Now, my question is this: What is the IEEE standard.I am working on a project that is working on the heat trace on our RWST's and this will be useful information to have if I can find it.
The IEEE standard that deals with heat trace and divisional power is IEEE 308-2001, Standard for Class 1E Power Systems for Nuclear Power Generating Stations.Section 7.6.10 of IEEE 308-2001 states that:> "Heat trace loads required for the post-accident operation of safety system components shall be supplied from the appropriate division of the Class 1E power system, except as permitted by 7.
6.10.1."Section 7.
6.10.1 states that:> "Heat trace loads associated with components whose failure can be tolerated for a duration of 72 hours following an accident (or longer, as demonstrated by plant-specific analysis) before compromising a safety function, may be powered from a non-Class 1E source provided that the following requirements are met:"> "(1) The heat trace load is protected by redundant, physically diverse non-Class 1E components."> "(2) The supply to the heat trace load is capable of being manually restored."> * "(3) The heat trace load is not required to prevent loss of safety function or damage to equipment required to perform a safety function."Therefore, under the conditions specified in IEEE 308-2001, the RWST heat trace may be powered from a non-1E source. The rationale for this is that the RWST is not required for the first 72 hours following an accident, and the heat trace is not required to prevent loss of safety function or damage to equipment required to perform a safety function. Flag for review