Question: someone told me that you can not have more than two penetrations on a disconnect but cant find it in the book, is this true and if so can you tell me the code.

Yes, this is true. According to the National Electrical Code (NEC), a disconnect shall not have more than two penetrations for conductors where the conductors enter or leave the enclosure.

NEC Reference

* 404.9 Penetrations

(A) Conductors Entering or Leaving Enclosures.
Conductors entering or leaving an enclosure shall be protected from abrasion and openings where they enter or leave, and shall not be subject to pinching or crushing. Where more than two conductors enter the enclosure through a wall or the roof, a listed enclosure shall be used for each conductor. Not more than two conductors shall be permitted to enter through the same opening. Flag for review