Question: Existing residential construction to be completely rewired in NM. Total of 3 floors above basement. Allentown, PA row home.My question is that there are two what look to have been forced air ducts going from basement all the way to 3rd floor that would make excellent chases to run romex in to get between floors preventing to have to cut as many holes in walls. The ducts are not connected to anything (in basement) and have been sealed over at the old exit points to rooms on 1st, 2nd, and 3rd floor. Heat is currently via radiators so no worries about these ducts being needed. Are there prohibitions to using these as chases? I plan to double check with local inspector about this on Monday unless ya'll know of reason not to use these ducts as chases.
NFPA 70 (National Electrical Code) 300.22 Raceways in Ducts Conductors shall not be installed in ducts or plenums used for the movement of air (except as permitted by 300.22(C)). 300.22(C) Exception for NM Cable NM cable shall be permitted to be installed in air-handling spaces as part of a dedicated system, provided that the NM cable is installed in accordance with the following: The NM cable is Type NM or NM-B. The NM cable is installed in a metal raceway. The metal raceway is grounded. The metal raceway is provided with metal covers. The NM cable is not installed in the same raceway with other conductors. The metal raceway is sized to contain the NM cable and any other conductors that may be installed in the raceway.
Other Considerations
Local Building Codes
Check with the local building inspector to ensure compliance with local codes.
Fire Safety
While the ducts are no longer in use, it's important to ensure that they are adequately sealed and any openings are firestopped to prevent the spread of fire or smoke.
Size of Ducts
The ducts must be large enough to accommodate the NM cable and any metal raceway that may be used.
Support
The NM cable and raceway must be properly supported within the ducts to prevent damage or movement.
Conclusion:
Using the old forced air ducts as chases for NM cable may be permissible under NFPA 70 and other guidelines, provided that the specific requirements outlined in the code are met. However, it's always recommended to consult with the local building inspector for specific guidance and approval. Flag for review