Question: Have a situation that happened Wednesday and am curious as to what you would require. We buy prefab communication buildings. The buildings come in all ready wired. They have a main disco inside that has TVSS systems tied to them. They then go through a ATS to a MDP. From the MDP a UPS is fed along with 2 HVAC units, lights and gen. use recpt. From the UPS are surge protected outlets. The feeders from the 40kw gen. were installed and it is a solid neutral system.The GC's that is in charge of the set up has his sub contractor elect. install a meter combo on the out side of the building and tie into the main disco inside. They also run and connect the gen. feeders.The communication tech's went there Wednesday to start their install. They turned on the main and things started smoking and snap,crackle and pop. One tech. ran like a girl, the other finally got his whits about him and killed the main after about 2-3 mins. of what in the world is going on.On Thursday my counter part went to look to find out what and who was responsible. When he opened the meter combo the first thing he saw was a 3/0 with about 4 inches of WHITE tape lugged in under the phase B of the main breaker. The neutral was in its proper place every where else.We know that the modules in the TVSS are shot, the HVAC unit tried to single phase. Some of the surge protected recpts. are gone along with lights that were fed from phase A. Chances are the electronic controls in the ATS and Gen. are gone also. Don't know about the 16kw UPS,it was in line position and did not have the modules or batteries in it yet.What would you require before you accepted the building? Megger the gen. to see if it hurt the armature? Megger the HVAC units? What check list would you want to see?
Required Documentation and Inspections
Investigation Report
A detailed report from the GC and electrical subcontractor explaining the sequence of events, cause of the incident, and corrective actions taken.
Electrical Inspection Report
A thorough inspection of the electrical system by a qualified electrician to verify that all wiring, components, and equipment are in proper working order.
Megger Reports
Megger tests to ensure that all electrical insulation is sound, including the generator armature and HVAC units.
Surge Protection Report
An assessment of the surge protection devices (TVSS) to determine their functionality and any damage sustained.
UPS Inspection Report
A visual and functional inspection of the UPS to verify its integrity and readiness for operation.
Checklist of Conditions for Acceptance
Remedial Repairs and Replacements
Confirmation that all damaged or malfunctioning components (TVSS, HVAC units, surge-protected receptacles, etc.) have been replaced or repaired.
Electrical Code Compliance
Verification that the electrical installation meets all applicable electrical codes and standards.
Grounding and Bonding
Inspection to ensure that the building is properly grounded and bonded.
Insulation Verification
Megger tests to confirm that the electrical insulation of all cables and equipment is satisfactory.
Generator Functionality
Demonstration that the generator operates correctly, including an automatic transfer switch test and load test.
HVAC System Verification
Confirmation that the HVAC units are functioning properly and are not damaged.
Surge Protection Functionality
Testing to verify that the surge protection devices are fully operational.
UPS Integrity
Assurance that the UPS is functioning properly and has sufficient battery capacity to provide backup power.
Additional Considerations
Communication Technology Inspection
Engage a communication technician to inspect and test the communication equipment to ensure it was not damaged by the electrical incident.
Documentation of Corrective Actions
Request detailed documentation of all corrective actions taken, including the specific components repaired or replaced.
Warranty Coverage
Confirm that any repairs or replacements are covered under warranty.*
Training and Education: Provide training to the GC and subcontractors on electrical safety procedures and proper handling of electrical equipment. Flag for review