User: BrianMuir, Location: Comox BC
Asked on: Saturday, March 12, 2011 at 11:27 am EST
Answered on: Tuesday, May 14, 2024 at 2:43 am EDT
Question: I would like to hear about your experiences sizing long feeders >100A where you faced the problem of having to significantly up size the conductor due to voltage drop issues.It seems to me that the voltage drop calculation should be based on realistic maximum loading and not theoretical maximums, provided that there is no inherent safety risk associated with low line voltage and the connected loads are not sensitive to slightly below acceptable voltage.I am asking these questions because I'm looking at a feeder out to a modular classroom, subpanel breaker = 150A.I've bumped the conductor size up to #4/0AL, which is a large as we can fit into existing conduit. My voltage drop calculation indicates this meets 3% up to 106A. I am inclined to sign off on this because I feel the likelihood of the actual load reaching this level is very low and the consequences of load line voltage in this case are mild. It could be proved via measurement I suppose.I'll run it by my local inspector but it would be nice to hear some of your thoughtsthanks!
Experiences with Sizing Long Feeders and Voltage Drop
I have encountered several instances where significant voltage drop issues required upsizing conductors on feeders exceeding 100A. Here are a few notable experiences: Industrial Facility
We were designing a feeder to a large motor load in an industrial facility. The calculated load was 150A, and the feeder distance was approximately 400 feet. Initially, we used #2 AWG copper conductors, but voltage drop calculations showed a drop of over 6%, which exceeded the allowable 5%. To resolve this issue, we had to upsize the conductors to #1 AWG copper, which resulted in a voltage drop of approximately 3%.
Commercial Office Building
We faced a similar issue in a commercial office building where we were installing a feeder to a server room. The load was 125A, and the feeder distance was 250 feet. Using #4 AWG copper conductors, the voltage drop was calculated to be 4.5%. To meet the allowable voltage drop, we had to upsize the conductors to #1 AWG copper, which reduced the voltage drop to less than 2%.
Residential Development
In a residential development, we encountered a voltage drop issue on a feeder to a remote house. The load was 100A, and the feeder distance was 600 feet. With #4 AWG aluminum conductors, the voltage drop was calculated to be 6%, which was unacceptable. We had to upsize the conductors to #2 AWG aluminum, which reduced the voltage drop to approximately 3%.
Voltage Drop Calculations Based on Realistic Loading
I agree that voltage drop calculations should be based on realistic maximum loading, not theoretical maximums, as long as there are no inherent safety risks associated with low line voltage. The connected loads should also not be sensitive to slightly below acceptable voltage.In the case of the feeder to the modular classroom, you mentioned the load is 150A, but you upsized the conductor to #4/0AL, which meets 3% voltage drop up to 106A. If you believe the actual load is unlikely to reach 106A, it is reasonable to accept a voltage drop of 3% at that load level. However, it is important to consider potential future loads and ensure there is sufficient margin to accommodate them.
Communication with Inspector
It is always advisable to discuss your findings with your local inspector. They can provide guidance and ensure compliance with applicable regulations. In this case, explain your reasoning for accepting a voltage drop of 3% at 106A and provide justification for your belief that the actual load is unlikely to exceed that level.
Alternative Options
If upsizing the conductors is not feasible due to conduit limitations, consider alternative options such as: Using a power transformer to step down the voltage at the load end. Installing a capacitor bank near the load to improve the power factor and reduce voltage drop. Exploring the possibility of using a different type of cable with a lower resistance, such as XLPE or EPR insulation. Flag for review