Question: When I am adjusting the ampacity of a raceway that all ready have 3 current carrying conductor do I have to derate more for spares and travelers?
Yes
The ampacity of a raceway with three or more current-carrying conductors must be derated for both spares and travelers. This is because spares and travelers increase the total number of conductors in the raceway, which results in increased heat generation and a reduced ampacity.The derating factor for spares and travelers is determined by the number of conductors in the raceway and the type of insulation on the conductors. For example, the derating factor for three current-carrying conductors plus one spare and one traveler is 80% for conductors with Type THHN insulation.When calculating the ampacity of a raceway with spares and travelers, the following steps should be followed:1. Determine the number of current-carrying conductors, spares, and travelers in the raceway.
2. Look up the derating factor for the number of conductors and type of insulation in the raceway.3. Multiply the ampacity of the raceway by the derating factor to obtain the adjusted ampacity. Flag for review