Question: Does the NEC allow mulitconductor cable 4/0 in larger in ventiliated cable tray without having to space the cable one cable diameter or greater, that is assume the multiconductor cables are installed in a single layer side by side with no spacing and do not exceed the tray widith? If so is the ampacity table 310.16 and no derating is required? Does the grounding conductor required to be single layer or can it be on top of the cables?
Can multiconductor cable 4/0 and larger be installed in a ventilated cable tray without spacing?
Yes. According to NEC 392.9(B)(2), multiconductor cables with conductors 4/0 AWG and larger may be installed in a single layer side-by-side in a ventilated cable tray without spacing.
Is the ampacity table 310.16 applicable and no derating required?
Yes. Provided that the multiconductor cables are installed in a single layer side-by-side in a ventilated cable tray, no derating is required and the ampacity table 310.16 can be used.
Can the grounding conductor be on top of the cables?
No. NEC 392.9(B)(2)(4) states that "If the cable tray contains single-conductor cables with insulated grounded conductors, the grounded conductors shall be installed in a single layer adjacent to the side of the tray." Therefore, the grounding conductor must be installed in a single layer next to the side of the tray, not on top of the cables. Flag for review