Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Code Question about Cable Tray

User: jsmith05, Location: Dallas, TX

Asked on: Saturday, March 12, 2011 at 3:12 pm EST
Answered on: Tuesday, May 14, 2024 at 2:44 am EDT

Question: Trying to determine if the proper sizing of the ampacity for 4/0 and larger MULTICONDUCTOR cable for use in a ventilated cable tray assuming single layer installation of the cables and not exceeding the tray width is to use Table 310.16 for ampacity of the individual conductors of the MULTICONDUCTOR cable? If so does the grounding conductor have to be counted or can it simply be on top of the phase conductors?Or are MULTICONDUCTOR cables 4/0 larger required to have 1 diameter between cables?

Ampacity Calculation for Multiconductor Cables in Ventilated Cable Trays

Yes, for multiconductor cables 4/0 and larger in a ventilated cable tray, the ampacity should be determined using Table 310.16 for the ampacity of the individual conductors of the cable.

Grounding Conductor

The grounding conductor does not need to be counted when calculating the ampacity of the multiconductor cable in a ventilated cable tray. However, it must be securely installed on top of the phase conductors, not within the cable bundle.

Spacing Requirements

For multiconductor cables 4/0 and larger in a ventilated cable tray, there is no specific requirement for spacing between cables. However, as per Section 318.11 of the National Electrical Code (NEC), the cables should be installed in a manner to provide adequate ventilation and heat dissipation. This means that the cables should not be bundled tightly together or placed in a way that restricts air circulation.

Summary:
Ampacity: Use Table 310.16 for the ampacity of the individual conductors of the multiconductor cable. Grounding: Install the grounding conductor on top of the phase conductors.* Spacing: Install cables to provide adequate ventilation and heat dissipation. Flag for review

Previous Question Next Question